Submitted by SorenAmroth t3_1197ety in DIY
SorenAmroth OP t1_j9kza4f wrote
Reply to comment by brock_lee in Circuit loses power GFCI by SorenAmroth
Need to report back Amperage the Circuit breaker is in panel later. By test u mean with my outlet tester?
I would need to recheck tester readings for all outlets while in off and on position. (Assuming you mean the Switched outlet )
The part idk is where in the circuit each sits. GFCI->switched outlet-> fridge. or Switched->gfci->fridge etc.
brock_lee t1_j9kznvv wrote
Yes, I was referring to testing the switched outlet. Sometimes people switch the neutral which can make for unexpected readings on a tester (and should be fixed). But, in the switched on position, if it reads the hot and neutral are reversed, they almost certainly are.
Viewing a single comment thread. View all comments