St1cks

St1cks t1_j190ivz wrote

The compressor doesn't cause the lower pressure side on its own. We use a type of metering device to achieve a flash off within the suction line. Ideally a 25/75 mix of liquid and gas should be present at the start of the evaporator coil. Metering devices can be fixed or adjusting, which generally use a sensing bulb attached at the inlet of the evaporator.

7