Wellcraft19 t1_ir4l1q7 wrote
Reply to comment by Loon610 in Wiring EV Charger by Loon610
You’re good and on the right track. I would just add that you’re not installing a ‘charger’ per se, but a fancy cable hanger.
The dip switches (good) are only there to communicate to the car (where the charger is located) how much current the car is allowed to draw. This so car [charger] does not draw more current than what the [house] infrastructure can support.
Level 2 ‘chargers’ are only a way to safely deliver 208/240 V AC to the car. People get overly hung on this [charger] and often spend far more than what they need. Or are a bit deceived of what the devices actually are and do.
But with a high static load (or high continuous load), it is imperative that all connections are properly done, are tight, as you will be pulling a decently high amperage for extended periods of time, and not like a clothes dryer (a comparable load) that often runs less than an hour, with load switching on and off during the time. A poor connection can easily overheat, leading to further heating. Etc.
Loon610 OP t1_ir5lswp wrote
Yeah I was reading more about EVSE vs charger yesterday. I didn’t really think of the charger in the car and the “charger” I’m installing is just a power supply. The good thing about the connections are the should be very simple. The connections at the breaker/panel, then straight to the EVSE with no splices and the charger is designed to be hardwired with terminal blocks and a bus bar.
Wellcraft19 t1_ir76gqf wrote
Like I said, you're good!